If a flooded system is operating with a suction pressure of 8 PSIG, what return line temperature would be concerning?

Prepare for the GCAP Operator 2 Test. Study with detailed questions and answers, including exam format and essential tips. Ace your exam with confidence!

In a flooded refrigeration system, the return line temperature is critical for ensuring the proper operation and efficiency of the system. If the suction pressure is 8 PSIG, the corresponding saturation temperature is approximately 20°F. In a well-functioning flooded system, the return temperature should ideally be above the saturation temperature to ensure that the refrigerant can evaporate properly and not result in flooding back to the compressor.

When the return line temperature reaches 0°F, it brings the system dangerously close to the saturation point. Although technically slightly above saturation, a return temperature at this point may indicate that the refrigerant is not fully evaporating in the evaporator, leading to potential liquid refrigerant returning to the compressor. This could cause compressor damage or a decrease in efficiency.

Therefore, a return line temperature of 0°F is cause for concern, as it may indicate that the system is at risk of producing too much liquid refrigerant reaching the compressor, potentially leading to operational issues.